HVAC Intake Extremely Loud

Problems related to residential installations.

HVAC Intake Extremely Loud

Postby albertngo » Wed May 03, 2017 7:27 pm

The loud intake vent is extremely loud. In the video link it is apparent that the sound is originating at the top of the vent and not the fan itself. I speculate it is the 90degree bend along with high wind speed that is causing the loud sound. Im no expert so any opinions will be greatly appreciated! Thanks!

*.be/4xV2j5uRQYU
albertngo
Minimal
 
Posts: 1
Joined: Wed May 03, 2017 7:21 pm

- HVAC Intake Extremely Loud

Postby HockingStevie » Mon May 08, 2017 8:39 am

Why is it so loud?
HockingStevie
Minimal
 
Posts: 1
Joined: Mon May 01, 2017 7:40 am

- HVAC Intake Extremely Loud

Postby Freon » Thu May 11, 2017 7:13 pm

You are thinking correctly. Many times the return air system is too small for the size of the AC system. As a result you have the blower trying too hard to bring return air back thereby creating a high velocity flow. Try and change the 90 degree to 2@45. Try and increase the diameter of the return duct. Anything that increases the cross section size of the duct or decreases any reatrictions (90 degree elbows) will help.
Freon
Most Valued Contributor
 
Posts: 1011
Joined: Sat Jun 18, 2011 11:26 am