- satic pressure tranducer

Posted: Sat Jan 15, 2011 1:12 pm
by juniorkarrie
I worked on 35 ton Trane Intellipak just the other day, and in this instance the Humidity control was controlled in one of two places. First the thermostat was programmed for humidity control with fan variations. Second there was seperate a Humidty control sensor located in the Return air Just before the Blower Assembly. As far as the Static Pressure Tranducer, well if it was factory installed, then your sensor should at the supply air veins past the Evap, Heat Exc, or Strips. If The Static pressure tranducer was not factory installed Then contact the Tech of startup and installation or the Duct design engineer beacause only they can tell you depending what perticullar duct there running placement might have been key. Hope this helps you.

- satic pressure tranducer

Posted: Tue Feb 13, 2018 1:17 pm
by JustMike
Typically, static pressure transducers or sensors are not factory installed. They are shipped loose to be installed in the duct work. The static pressure transducers are usually installed 2/3 of the way down the main duct. The placement being further down into the duct is important to maintain enough air at the end of the duct runs.